Cigar Asylum Cigar Forum  

Go Back   Cigar Asylum Cigar Forum > Non Cigar Specialty Forums > Misc > General Discussion

Reply
 
Thread Tools Display Modes
Old 02-10-2010, 06:41 PM   #21
shilala
Dear Lord, Thank You.
 
shilala's Avatar
6
 
Join Date: Oct 2008
First Name: Scott
Posts: 13,721
Trading: (252)
Cuaba
shilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond repute
Default Re: Question for an electrician - HELP!

Brian, if your breaker box is in the crawl space, and you have empty spaces for breakers, it doesn't get any easier than running some romex and setting some surface mount outlets on a dedicated circuit.
That would take the load off and wouldn't cost but a couple bucks for material.
I wish I was closer, we could knock it out in no time.
Even if you hired a guy to do it, it's not a big job at all. It'll take longer to drag tools back in the crawl space than to get it done. Literally.
Have someone take a look at what you need done. Tell him you want a dedicated circuit and some easy to place surface mount outlets. Just a couple would help. Three would really take the load off.
If you got really fancy, you could set a couple circuits worth of outlets and never have a problem again.
Mind ya, I'm imagining a ranch style with the breaker box in the crawl space. Even if it's two story, breakers on the floor above the crawl space would help, I'd think.
It really depends on the layout of the house and the extent of the crawl space.
__________________
shilala is offline   Reply With Quote
Old 02-11-2010, 07:38 PM   #22
Hitagain
Bomb'n relocation program
 
Join Date: Feb 2009
First Name: Allen
Location: St. Louis
Posts: 103
Trading: (7)
SCdlH
Hitagain is on a distinguished road
Default Re: Question for an electrician - HELP!

Quote:
Originally Posted by Starz26 View Post
3. Add up all your breakers and make sure they do not go over the total amps for your service.


If you have a 42 circuit 200 amp panel, you could install 42 20 amp breakers if you want. This is because most circuits are not continuous loads.
Breakers are sized to protect the wire. Wire is sized to serve the load.

DO NOT PUT A 30 BREAKER TO FEED 15/20 AMP OUTLET.
__________________
I.B.E.W. Local 1
Hitagain is offline   Reply With Quote
Old 02-12-2010, 03:57 PM   #23
beamish
Guest
 
Posts: n/a
Default Re: Question for an electrician - HELP!

Quote:
Originally Posted by Hitagain View Post
If you have a 42 circuit 200 amp panel, you could install 42 20 amp breakers if you want. This is because most circuits are not continuous loads.
Breakers are sized to protect the wire. Wire is sized to serve the load.

DO NOT PUT A 30 BREAKER TO FEED 15/20 AMP OUTLET.
what he said...more than likely you need to run additional circiuts to split the loads..the size of the service doesnt really matter if you have 100a you can always add a sub panel 100 amps you are allowed 24 poles [circuit breakers] however they do now make 30 circuit 100 amp panels,when your house was built, it was not wired to accept all the load demands of today , especially plugging in heaters, like mentioned before breakers size is directly related to the size of the wire #12 wire is rated for more than 20 amps but a 20 amp breaker is all the code allows etc...placing a larger breaker in place to solve the tripping problem is a sure fired way to a fire ....the problem is probably due to internal house wiring problems ,[to many things plugged into said circuits..the only way to fix this problem is to run new circuits to the affected areas and split up the loads ..hit the laundry with a 20 amp circuit
the idea is to get the heavy hitting appliances on their own,,micro,,coffee..laundry...etc...the original circuit is probably fine for general items like tv,,lamps stereo..etc.....for now dont run to many things at once...hope this helps...
  Reply With Quote
Old 02-13-2010, 10:11 AM   #24
cf2112
Guest
 
Posts: n/a
Default Re: Question for an electrician - HELP!

Some seriously bad advise given here (a few with good advise). Hire an Electrician and pay him to do the work or you could burn your house down and/or die. I've been an electrician for 25 years and have seen homeowners fu** up more wiring than you can imagine. We are currently rewiring a house that burned because they doubled/tripled up circuits on oversized breakers. Wire size determines breaker size. Why risk your families safety getting advise from cigar smokers or off the internet.

Do your own plumbing get wet, do your own electrical you can die.

If your breaker box is a Federal Pacific or Zinsco GET IT CHANGED NOW, google Federal Pacific or Zinsco breaker to see what I mean. This should run $1500-2500.
http://www.inspectapedia.com/fpe/fpepanel.htm
http://www.inspectapedia.com/electric/Zinsco.htm
  Reply With Quote
Old 02-13-2010, 10:40 AM   #25
BORIStheBLADE
_
 
BORIStheBLADE's Avatar
 
Join Date: Nov 2008
First Name: Mike
Location: Santa Clara, CA
Posts: 643
Trading: (4)
Bolivar
BORIStheBLADE will become famous soon enough
Default Re: Question for an electrician - HELP!

You can get some really good ideas on the internet from people about your options and how to go about them, but the reality is the potential for you to get hurt or killed is pretty high given your knowledge of electrical.

Me personally.... if you don't know anyone that is an electrician I would hire a local electrician to come buy and spend an hour or two investigating your options and whats going on.

He will know how to open the panel and close it up. It sounds simple, but if the past owner hired a shotty electrician he could have created a hazard behind the panel cover and done something to get by which in reality you wouldn't know whats up or how to react to it.

I've been an electrician for 12 years so thats my
__________________
I.B.E.W LOCAL # 617
BORIStheBLADE is offline   Reply With Quote
Old 02-13-2010, 11:09 AM   #26
Starz26
Adjusting to the Life
 
Starz26's Avatar
 
Join Date: Aug 2009
First Name: Eric
Location: Ohio
Posts: 486
Trading: (22)
Army (Served With Honor)
Starz26 will become famous soon enough
Default Re: Question for an electrician - HELP!

Quote:
Originally Posted by cf2112 View Post
Some seriously bad advise given here
I resemble that remark......

Thank for all the good information posted here...I learned a lot...
Starz26 is offline   Reply With Quote
Old 02-13-2010, 11:46 AM   #27
cf2112
Guest
 
Posts: n/a
Default Re: Question for an electrician - HELP!

No offense meant to anyone. Somethings are best left to those who are trained in the field you need. Safety should always trump cost.

I own rental properties and can do alot of different repairs but almost always hire a certified contractor. I know it costs more but the safety of my family and the families I rent homes to is more important than saving a few $$. I hire my own company to do any electrical on my rentals and rarely work on them myself, mainly for liability and the inspection that goes with it.

A good friend just installed his own water heater in a rental he owns, it leaked causing some major damage. His insurance is pitching a fit and refusing to pay for lost rent since he did the work himself and did not get it inspected. You are allowed to do work on your own house (if you get it inspected) but not any rental property.
  Reply With Quote
Old 02-13-2010, 12:21 PM   #28
Rabidsquirrel
Moderately Confused
 
Rabidsquirrel's Avatar
 
Join Date: Oct 2008
Location: Pennsylvania, US
Posts: 576
Trading: (5)
Rabidsquirrel is on a distinguished road
Default Re: Question for an electrician - HELP!

If it says Federal Pacific, don't even open anything. It's not worth dying over.
Rabidsquirrel is offline   Reply With Quote
Old 02-13-2010, 03:03 PM   #29
cbsmokin
Looking for the Apex
 
cbsmokin's Avatar
 
Join Date: Oct 2008
First Name: Craig
Location: In da ATL
Posts: 880
Trading: (10)
Cohiba
cbsmokin will become famous soon enough
Default Re: Question for an electrician - HELP!

Good luck with your project. i'd love to see some pictures of the place.
__________________

Check out C.A.R.B. IV http://www.cigarasylum.com/vb/showth...840#post879840
cbsmokin is offline   Reply With Quote
Old 02-13-2010, 07:25 PM   #30
Drat
Guest
 
Posts: n/a
Default Re: Question for an electrician - HELP!

Thanks for all of the replies, both good and bad advice

The friend we were helping out moved out of the attic and the breaker can easily handle the load now that there isn't a computer, clock, heater, and god-knows whatever else he had plugged into that attic outlet.

It's still a concern that needs to be addressed, but not immediately (my lack of funds really appreciates that).

I'm smart enough not to tackle repairs that I know nothing about, especially when it comes to electricity. I've taken enough shocks from car batteries to know that I don't like getting shocked. Burning down our house because I wanted to save a couple of dollars is ridiculous.

As it stands, I'll probably have somebody out in spring to look at the box and see if there are any options outside of wiring in new outlets to the areas where there will be higher draws.

The house is 90 years old, but from the looks of the wiring in here, it looks like they rewired it sometime within the last 30 years.

Luckily the crawlspace is about 4.5' high, so it's not real difficult to get around down there. I'm building my homebrew draft system down there in 2 weeks (running the lines up into the liquor cabinet on the floor above). I've got my priorities straight
  Reply With Quote
Old 02-13-2010, 07:50 PM   #31
Silound
ex-CS Swamp Gorilla
 
Silound's Avatar
 
Join Date: Nov 2008
Location: Somewhere in a swamp, south of sanity
Posts: 802
Trading: (15)
Bolivar
Silound will become famous soon enough
Default Re: Question for an electrician - HELP!

Quote:
Originally Posted by cf2112 View Post
Some seriously bad advise given here (a few with good advise). Hire an Electrician and pay him to do the work or you could burn your house down and/or die. I've been an electrician for 25 years and have seen homeowners fu** up more wiring than you can imagine. We are currently rewiring a house that burned because they doubled/tripled up circuits on oversized breakers. Wire size determines breaker size. Why risk your families safety getting advise from cigar smokers or off the internet.

Do your own plumbing get wet, do your own electrical you can die.

If your breaker box is a Federal Pacific or Zinsco GET IT CHANGED NOW, google Federal Pacific or Zinsco breaker to see what I mean. This should run $1500-2500.
http://www.inspectapedia.com/fpe/fpepanel.htm
http://www.inspectapedia.com/electric/Zinsco.htm

That.....DISTURBS me....greatly. Almost every house I've lived in have Federal breaker boxes in them. Is that a problem specific to a range of models or dates, or is that a general problem for all FPE boxes?
__________________
Back in black, and better than ever! You can't keep a good gorilla down!
LSU Geaux Tigers!
Silound is offline   Reply With Quote
Old 02-13-2010, 11:25 PM   #32
cf2112
Guest
 
Posts: n/a
Default Re: Question for an electrician - HELP!

If it's a FPE BREAKER box change it, we call them the "Fire Starter". They went out of business rather than be sued out of business. Fuse panels re not as bad if they are fused correctly but everyone uses 30 amp fuses instead of fusing according to wire size.
  Reply With Quote
Old 02-14-2010, 08:40 AM   #33
Rabidsquirrel
Moderately Confused
 
Rabidsquirrel's Avatar
 
Join Date: Oct 2008
Location: Pennsylvania, US
Posts: 576
Trading: (5)
Rabidsquirrel is on a distinguished road
Default Re: Question for an electrician - HELP!

Anything FP made is a deathtrap. Nobody in the local while throw a breaker on the switchgear if it's energized, let alone work on it.
Rabidsquirrel is offline   Reply With Quote
Old 02-14-2010, 09:16 AM   #34
rack04
Lebowski Urban Achiever
 
Join Date: Oct 2008
First Name: Justin
Location: Dallas, TX
Posts: 1,023
Trading: (20)
HUpmann
rack04 will become famous soon enoughrack04 will become famous soon enough
Default Re: Question for an electrician - HELP!

The house we just bought had a 100 amp FPE panel. It was noted as a fire hazard during the inspection. I had an electrical change out the panel and upgrade the service to 200 amp. $1600 for piece of mind was well worth it.
__________________
"Why don't you put them in your secret compartment" - 12stones (Ricky)
rack04 is offline   Reply With Quote
Old 02-14-2010, 09:16 AM   #35
cf2112
Guest
 
Posts: n/a
Default Re: Question for an electrician - HELP!

Quote:
Originally Posted by Rabidsquirrel View Post
Anything FP made is a deathtrap. Nobody in the local while throw a breaker on the switchgear if it's energized, let alone work on it.
They made an ok fuse panel (see above comments on fuse panels) but the "stab-lock" breakers are a fire hazard.

We reccomend replacement, if they can not afford it or do not want to do it we make them sign a letter stating we asked, gave a price and they refused. About 50% will call back and have us replace the panel within a week.
  Reply With Quote
Old 02-16-2010, 12:33 PM   #36
shilala
Dear Lord, Thank You.
 
shilala's Avatar
6
 
Join Date: Oct 2008
First Name: Scott
Posts: 13,721
Trading: (252)
Cuaba
shilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond reputeshilala has a reputation beyond repute
Default Re: Question for an electrician - HELP!

Quote:
Originally Posted by Rabidsquirrel View Post
If it says Federal Pacific, don't even open anything. It's not worth dying over.
My stepmother lost two bedrooms and four or five months in her house over a Federal breaker panel. Fortunately no one was hurt and they caught the fire quick.
For no apparent reason, it just cooked one of the bus bars and melted right through the back of the panel.
__________________
shilala is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -6. The time now is 11:17 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
All content is copyrighted jointly by Cigar Asylum and the content provider.