View Single Post
Old 09-04-2009, 03:37 PM   #30
BigFrank
5 3 1
 
BigFrank's Avatar
 
Join Date: Nov 2008
First Name: Frank
Location: Gym or Sofa.
Posts: 1,896
Trading: (25)
Partagas
BigFrank will become famous soon enough
Default Re: Electrician question?

General Installation Requirements
406.3(D)(3)
Non-Grounding-Type Receptacles
-Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with...

a. A non grounding type receptacle shall be permitted to be replaced with another non grounding type receptacle.

b. A non grounding type receptacle shall be permitted to be replaced with a GFCI type of receptacle. These receptacles shall be marked "no equipment ground". An equipment grounding conductor shall not be connected from the GFCI type receptacle to any outlet supplied from the GFCI receptacle.

c. A non grounding type receptacle shall be permitted to be replaced with a grounding type receptacle where supplied through a GFCI. Grounding type receptacles supplied through the GFCI shale be marked "GFCI protected" and " No equipment ground" An equipment grounding conductor shall not be connected between the grounding type receptacles.



Had to look something up tonight job related so there ya go.
__________________
" Hope is the first step on the road to disappointment. "
BigFrank is offline   Reply With Quote